SUPPLY PANEL FEEDER BREAKER ATTACHED TO BUS BAR AND NOT AT TOP OF BREAKER
fun ee
Texas
Can a feeder supplying power to panel be connected to a branch circuit breaker or does NEC 408.36 or any other code paragraph disallow this?
Thanks Again.
I may misunderstand the question, but a breaker is not in itself a branch or feeder breaker.
A 50 amp breaker would be the same for a feeder or a branch circuit.... it depends on how it's used... see the definition of a branch circuit and feeder.
I assumed the OP was asking if it can be used as a main disconnect. Yet, I haven?t looked at the NEC section in question
The code section mentioned requires an OCPD at any point along the path of the panel feeder. The panel itself does not require a main OCPD.