- Lockport, IL
- Retired Electrical Engineer
I am having a disagreement with an engineer whose design I am reviewing. It boils down to this: (1) What exactly is an SSBJ, (2) What exactly does it do for a living, and (3) Can you accomplish what it does for a living by having metal conduit from service transformer to the main service panel and by bonding that conduit to enclosures at both ends using a “wire” that is just a few inches long and is sized per 250.102(C)? He says yes. I had understood (perhaps incorrectly) that the SSBJ was to be run inside the conduit along with all the other conductors.
Part of his argument came from the 2011 Handbook. Here is his statement: “The 2011 NEC Handbook provides an application example specifically describing bonding multiple raceways---not running an addition conductor in the raceway(s).” My only copy of the Handbook is at my office, and I am not permitted to go there while the virus is doing its thing. I suspect he might be taking what the handbook says out of context.
Can someone explain the situation to me? Can someone post (without violating copyrights) that portion of the Handbook?