Can supply side bonding jumper be screw or it has to be wire? I don’t see where in code it says this.
You just ask for a long and flexible screw with treads on the end.How would you use a screw for a SSBJ?
"250.2 SSBJ A conductor................................."It would be quite rare to be in a situation where one could use a screw as a SSBJ, although there is no definition of a SSBJ in the NEC (unless they've added one after 2014?). Say one had a neutral terminal bar attached to a service pull box or trough. Could the screw holding that bar to the box be considered an SSBJ?
I'd say if designed and listed that way yes.It would be quite rare to be in a situation where one could use a screw as a SSBJ, although there is no definition of a SSBJ in the NEC (unless they've added one after 2014?). Say one had a neutral terminal bar attached to a service pull box or trough. Could the screw holding that bar to the box be considered an SSBJ?
"250.2 SSBJ A conductor................................."
It would be quite rare to be in a situation where one could use a screw as a SSBJ, although there is no definition of a SSBJ in the NEC (unless they've added one after 2014?). Say one had a neutral terminal bar attached to a service pull box or trough. Could the screw holding that bar to the box be considered an SSBJ?
I'd say if designed and listed that way yes.
Midwest terminal boxes we use often on farms have terminals mounted in insulating blocks. They come with a copper bonding jumper, probably about a 2 AWG solid copper conductor in most 200 amp versions and a lug bolted to the box to land it in. That lug is only tapped into the box with a 10-32 screw though. Never seen one burn off, but have seen 1/4 bond screws in 200 amp panelboard neutral bus burn off where tapped into enclosure, probably because they were not properly tightened.
And that screw was probably designed and tested for the application, you can't just put any screw in there. Just like the screws that are used to bond panelboard neutral assemblies.It was a while ago, but I am pretty sure I did 1000 amp CT cabinet that had an isolated neutral bar, and a screw could be used to bond it to the cabinet like in a typical load center. I would say that is a SSBJ per Augies definition.
And that screw was probably designed and tested for the application, you can't just put any screw in there. Just like the screws that are used to bond panelboard neutral assemblies.
I'd say the bar itself is.Say one had a neutral terminal bar attached to a service pull box or trough. Could the screw holding that bar to the box be considered an SSBJ?
I'd say the bar itself is.
Don't make this anymore complicated than needed. Just bolt a multi port lug with enough ports for your neutrals and GEC directly to the wireway. If you need more ports you can stack another multi port lug on top. They just need to all be stacked with one bolt attaching them so you are not using the enclosure as a conductor. No bonding jumper needed.I have neutral terminal in splice box line side of service trough. The trough feeds multiple disconnect enclosures downstream. Grounding electrode system would be at this splice box neutral bar. Neutral bar needs to be bonded to enclosure. Dont follow would a screw holding bar considered SSBJ?
Sent from my iPhone using Tapatalk
Don't make this anymore complicated than needed. Just bolt a multi port lug with enough ports for your neutrals and GEC directly to the wireway. If you need more ports you can stack another multi port lug on top. They just need to all be stacked with one bolt attaching them so you are not using the enclosure as a conductor. No bonding jumper needed.
Just bolt the lug(s) directly to the enclosure. The neutral is now bonded to the enclosure.Don’t the enclosure which is metal and on line side of service disco need to be bonded to neutral which is my grounded conductor?