hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
Attached sketch shows 480/277V three phase 2 sets of 4#500 kcmil service conductors into trough. The service conductors are connected three times by 4#3/0 AWG which feed three main service disconnects fused at 200A.
Each main service disconnect inside has supply side bonding jumper which bonds the service metallic conduit. However at the other end of the conduit service trough side their is also supply side bonding jumper which bond metallic conduit to trough all sized #4 AWG.
The question is is the supply side bonding jumper from trough neutral conductor to the trough enclosure shown inside trough is still require or the supply side bonding jumper from each conduit to service trough sufficient ? It’s marked in sketch “Is this still needed?”