hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
I have wire-way in line side of 4 main service discos. The wire has wire one set of 1 set of 4-600 kmil to each of service disconnect.
The engineer has provided what he calls supply side bonding jumper from each service disconnect ground bus to the wire-way enclosure #2/0 awg.
I have the following questions:
1. Is the bonding jumper mentioned from each service disconnect to the wireway enclosure allowed to be in conduit with phase and neutral conductors between wireway and service disconnect or not?
2. Can it be outside the wireway?
3. Should not the wireway be bonded with bonding jumper from neutral to the wire way enclosure in line side instead of supply side bonding jumper?
The engineer has provided what he calls supply side bonding jumper from each service disconnect ground bus to the wire-way enclosure #2/0 awg.
I have the following questions:
1. Is the bonding jumper mentioned from each service disconnect to the wireway enclosure allowed to be in conduit with phase and neutral conductors between wireway and service disconnect or not?
2. Can it be outside the wireway?
3. Should not the wireway be bonded with bonding jumper from neutral to the wire way enclosure in line side instead of supply side bonding jumper?