I have an outdoor MV transformer (Delta - Wye) that feeds an indoor MV switchgear with a main disconnect. It will have (5) parallel feeds from the transformer to the SWGR. Am I right to do the following:
1. Tie X0 to the grounding electrode outdoor. Tie X0 to indoor SWGR Neutral. Indoor Neutral will be completely isolated from the MV SWGR chassis/ground.
2. Tie indoor MV Chassis/Ground to the grounding electrode system. I am under the impression that under 250.102(E)(2), I can run a single supply side bonding jumper outside of the raceways as long as it is limited to 6 feet. I have a 500MCM tied to the grounding electrode and it is about 30 feet in length which will stubup inside the indoor MV swgr. Will this entire length 500MCM be considered as grounding electrode or supply side bonding jumper? If it is considered as supply side bonding jumper, then I would have to run the bonding jump in the same raceways as my current carry conductors?
Any comments are appreciated.
1. Tie X0 to the grounding electrode outdoor. Tie X0 to indoor SWGR Neutral. Indoor Neutral will be completely isolated from the MV SWGR chassis/ground.
2. Tie indoor MV Chassis/Ground to the grounding electrode system. I am under the impression that under 250.102(E)(2), I can run a single supply side bonding jumper outside of the raceways as long as it is limited to 6 feet. I have a 500MCM tied to the grounding electrode and it is about 30 feet in length which will stubup inside the indoor MV swgr. Will this entire length 500MCM be considered as grounding electrode or supply side bonding jumper? If it is considered as supply side bonding jumper, then I would have to run the bonding jump in the same raceways as my current carry conductors?
Any comments are appreciated.