The topic of bonding the grounded conductor at the disconnect for a PV supply side connection has come up so frequently, I had to put together an FAQ document for my inspection coordinators to refer to when getting push back from inspectors. Somebody, somewhere, started the rumor that this disconnect should not be treated as a service disconnect.
The code is fairly explicit in describing the conductors that feed this enclosure as a "set" of service entrance conductors.
(230.40, exception 5). I really don't see where the confusion lies. Yet, another inspector is asking that we remove the main bonding jumper and isolate the neutral as in a subpanel, a violation of 250.24(B), 250.28.
Other relevant articles:
Art 100 - Definitions, see Service,Service Conductors, and Service Equipment.
705.12(A)
230.82(6)
Not one of these inspectors has cited a code article that prohibits the bonding of the neutral, they all parrot the same line..."it's not a service". Correct, it is not a seperate service, it is a service disconnect, and the neutral is required to be bonded.
Can one of you kind folks let me know if I'm way off base here? And if you are going to argue that it's not a service disconnect, please reference a code artricle.
The code is fairly explicit in describing the conductors that feed this enclosure as a "set" of service entrance conductors.
(230.40, exception 5). I really don't see where the confusion lies. Yet, another inspector is asking that we remove the main bonding jumper and isolate the neutral as in a subpanel, a violation of 250.24(B), 250.28.
Other relevant articles:
Art 100 - Definitions, see Service,Service Conductors, and Service Equipment.
705.12(A)
230.82(6)
Not one of these inspectors has cited a code article that prohibits the bonding of the neutral, they all parrot the same line..."it's not a service". Correct, it is not a seperate service, it is a service disconnect, and the neutral is required to be bonded.
Can one of you kind folks let me know if I'm way off base here? And if you are going to argue that it's not a service disconnect, please reference a code artricle.