What is everyone's take on these type of service panels? We call them Power Packs and they're very common up in the Panhandle (Florida).
It's my understanding that if we put a backfeed breaker here it would be consider a supply side connection since there is no actual "service disconnecting means" between the meter and the busbar. If my PV system is the only power production source connected here, per 705.12(A) my backfeed breaker can be as big as whatever the service is rated for, since technically I'm on the supply side. However, if the sum of the other breakers goes over the service rating, wouldn't that post a risk of overloading the busbar in a worst case scenario (eg: all these other breakers pull whatever they're rated for at the same time)?