what other examples come to mind? I wish it was defined. It not being defined means it would have the same definition as in a regular dictionary right?I think it has more to do with being ahead of the OCPD like in a SSBJ (supply side bonding jumper).
Bonding Jumper, Supply-Side.
A conductor installed on the supply side of a service or within a service equipment enclosure(s), or for a separately derived system, that ensures the required electrical conductivity between metal parts required to be electrically connected.
It’s always good when the definition contains one of the words it’s defining lolThis might get you close but it's certainly not comprehensive as far as definitions go.
I think it is a commonly understood term and does not need to be in Article 100. I also doubt you would find a reasonable definition in Webster’s Collegiate Dictionary, 11th edition, the specified dictionary in the NEC Style Manual.what other examples come to mind? I wish it was defined. It not being defined means it would have the same definition as in a regular dictionary right?
Would you consider it synonymous with upstream?I think it is a commonly understood term and does not need to be in Article 100. I also doubt you would find a reasonable definition in Webster’s Collegiate Dictionary, 11th edition, the specified dictionary in the NEC Style Manual.
I would see that as being the same, but the correct term is supply side.Like if I said, upstream of the service disconnect, would that be the same as supply side of the service disconnect?
Is the supply side of a transformer the primary side?I would see that as being the same, but the correct term is supply side.
I do think the ssbj messed me up because it’s on the secondary side for a sdsI think it has more to do with being ahead of the OCPD like in a SSBJ (supply side bonding jumper).
Upstream of the disco is the same as the supply side of the disco.Like if I said, upstream of the service disconnect, would that be the same as supply side of the service disconnect?
It is on the supply side of the OCPD.I do think the ssbj messed me up because it’s on the secondary side for a sds
okay I think I got it thank youUpstream of the disco is the same as the supply side of the disco.
Upstream in general only means towards the supply side of a given point.
Which is why a SSBJ is typically larger than the EGC on the load side of the OCPD. For example the SSBJ for a 400 amp OCPD on the secondary of a transformer i3th 600 kcmil conductors would be a minimum of #1/0. The EGC on the load side of the same 400 amp OCPD would only need to be a minimum of #3.It is on the supply side of the OCPD.
Another question. How does the first ocpd after a transformer protect its supply conductors. Wouldn’t it just protect the conductors downstream of itself?Which is why a SSBJ is typically larger than the EGC on the load side of the OCPD. For example the SSBJ for a 400 amp OCPD on the secondary of a transformer i3th 600 kcmil conductors would be a minimum of #1/0. The EGC on the load side of the same 400 amp OCPD would only need to be a minimum of #3.
Same way a main breaker effectively protects its supply conductors, similar to allowances for tap rules.Another question. How does the first ocpd after a transformer protect its supply conductors. Wouldn’t it just protect the conductors downstream of itself?
It only protects against overloading. Short circuits or ground faults ahead of it will not be detected at all by that device. If things are designed correctly the overcurrent protection on primary side should still respond to short circuits/ground faults on the secondary, but depending on conditions it may not be as fast of response as if a short circuit or ground fault occurred in the primary conductors as you do have impedance of the transformer in the circuit. This big factor in the reason for the tap rules associated with the conductors on the secondary.Another question. How does the first ocpd after a transformer protect its supply conductors. Wouldn’t it just protect the conductors downstream of itself?
What happens in the primary if say there’s a bolted short on the secondary?It only protects against overloading. Short circuits or ground faults ahead of it will not be detected at all by that device. If things are designed correctly the overcurrent protection on primary side should still respond to short circuits/ground faults on the secondary, but depending on conditions it may not be as fast of response as if a short circuit or ground fault occurred in the primary conductors as you do have impedance of the transformer in the circuit. This big factor in the reason for the tap rules associated with the conductors on the secondary.