Just like the service OCPD, it only provides overload protection. It does not provide ground fault and short circuit protection. That is why the length of the transformer secondary conductors is limited and why the service OCPD, if inside, must be "nearest the point of entrance" of the service conductors.Another question. How does the first ocpd after a transformer protect its supply conductors. Wouldn’t it just protect the conductors downstream of itself?
Overload protection can be provided at any point on the circuit, but short circuit and ground fault protection can only be provided at the supply end of the conductors.