Is it always absolutely necessary to parallel MV buses when supplying spot and secondary network feeders? No phase angle differences on the 138kv bus.


Certain scenarios will require a bus section to be taken out of service (network stays on through N-2) breaking the normally closed topology. I'd like to eliminate running bus or cable to tie the two ends together forming a ring.
 

Tony S

Senior Member
A parallel bus is designed for redundancy the same as parallel feeders.

Our 132kV site supply had interconnects for the 132kV, 33kV and 11kV busbars. A belt and braces expensive approach but secure. Furnaces full of solid iron due to a power failure are even more expensive.
 

Sahib

Senior Member
Location
India
Unlike radial distribution, power supply could remain unaffected in one section for a fault in another section in a ring distribution.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
A parallel bus is designed for redundancy the same as parallel feeders.

Our 132kV site supply had interconnects for the 132kV, 33kV and 11kV busbars. A belt and braces expensive approach but secure. Furnaces full of solid iron due to a power failure are even more expensive.

Would you say two parallel busbars would be better over 6 busbars interconnected with tie breakers?



Unlike radial distribution, power supply could remain unaffected in one section for a fault in another section in a ring distribution.



I know- but being a network in theory it should survive with one section of busbar taken out. Issue is the phase angles resulting. Here is what I am dealing with:
 

Attachments

  • network substation.jpg
    network substation.jpg
    80.5 KB · Views: 0

Sahib

Senior Member
Location
India
I know- but being a network in theory it should survive with one section of busbar taken out. Issue is the phase angles resulting. Here is what I am dealing with: