Trying to figure out if an independent support wire is used to support cable shall it it be secured at each end and what does secure at each end mean? Attached to structure and the ceiling grid?
300.11 Securing and Supporting.
(B) Wiring Systems Installed Above Suspended Ceilings. Where independent support wires are used, they shall be secured at both ends. Cables and raceways shall not be supported by ceiling grids.
(2) Non–Fire-Rated Assemblies. Wiring located within the cavity of a non–fire-rated floor–ceiling or roof–ceiling assembly shall not be secured to, or supported by, the ceiling assembly, including the ceiling support wires. An independent means of secure support shall be provided and shall be permitted to be attached to the assembly.
The 2017 Commentary states this:
Independent support, and securing both ends of the support wire, do preclude a connection to the ceiling grid on one end.The word Preclude basically means makes it impossible so which is it ? Secure both ends or is it impossible? How would it be secure if you didn't attach it to the grid?