zcanyonboltz
Senior Member
- Location
- denver
Where in 2014 NEC is secure and support requirements for #4, #6 bare copper or number #2 aluminum in a residential building for grounding or say 4/0 copper not in a raceway? Thanks
Where in 2014 NEC is secure and support requirements for #4, #6 bare copper or number #2 aluminum in a residential building for grounding or say 4/0 copper not in a raceway? Thanks
(2) Grounding and Bonding Conductors. Equipment grounding conductors shall be permitted to be installed outside
a raceway or cable assembly where in accordance with the provisions of 250.130(C) for certain existing installations
or in accordance with 250.134(B), Exception No. 2,for dc circuits. Equipment bonding conductors shall be permitted to be installed on the outside of raceways in accordance with 250.102(E). (3) Nonferrous Wiring Methods
I was pointed in the same direction....maybe 300.3 ?
Where in 2014 NEC is secure and support requirements for #4, #6 bare copper or number #2 aluminum in a residential building for grounding or say 4/0 copper not in a raceway? Thanks
There are no support requirements for GECs, that is why they cannot be found.