Where in 2014 NEC is secure and support requirements for #4, #6 bare copper or number #2 aluminum in a residential building for grounding or say 4/0 copper not in a raceway? Thanks
 
I'm sure someone will cite chapter & verse....Pull the wire taut, & staple to joist or mud sill. Run the wire through bored holes if that works for you. Remember to protect your wire where subject to damage.
 
Last edited:
I have been looking and cannot find a requirement. Table 300.19 (A) came to mind but this is for vertical runs in raceways, I cannot find a requirement for bare ground or insulated single conductors of copper or aluminum. One staple not more than 4.5 feet like romex is what I've been doing but for long runs and having the wire tight this overkill just would like to know if it is in the 2014 NEC. I mean you can make romex look good with a staple every 10 feet on long runs like say stapled to a truss or TGI.
 
maybe 300.3 ?

(2) Grounding and Bonding Conductors. Equipment grounding conductors shall be permitted to be installed outside
a raceway or cable assembly where in accordance with the provisions of 250.130(C) for certain existing installations
or in accordance with 250.134(B), Exception No. 2,for dc circuits. Equipment bonding conductors shall be permitted to be installed on the outside of raceways in accordance with 250.102(E). (3) Nonferrous Wiring Methods
 