Support fixture whips; 330.11 (D)2 or 300.11

Status
Not open for further replies.

Finite10

Senior Member
Location
Great NW
Which is superior; 330.11 (D)2 or 300.11 when supporting fixture whips?

300.11 says 'Cables and raceways shall not be supported by ceiling grids.
But 330.11(D)2 specificall addresses MC connectors as a support. BUT! Fixture whips are often not MC with MC connectors. They're listed 6 ft whips for fixtures, often.

Just wondering what the concensus if here.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
If the whips are constructed from FMC then you can up to 6' unsupported.

348.30 Securing and Supporting.
FMC shall be securely fastened in place and supported in accordance with 348.30(A) and (B).
(A) Securely Fastened. FMC shall be securely fastened in place by an approved means within 300 mm (12 in.) of each box, cabinet, conduit body, or other conduit termination and shall be supported and secured at intervals not to exceed 1.4 m (4? ft).
Exception No. 1: Where FMC is fished between access points through concealed spaces in finished buildings or structures and supporting is impractical.
Exception No. 2: Where flexibility is necessary after installation, lengths shall not exceed the following:
(1) 900 mm (3 ft) for metric designators 16 through 35 (trade sizes ? through 1?)
(2) 1200 mm (4 ft) for metric designators 41 through 53 (trade sizes 1? through 2)
(3) 1500 mm (5 ft) for metric designators 63 (trade size 2?) and larger
Exception No. 3: Lengths not exceeding 1.8 m (6 ft) from a luminaire terminal connection for tap connections to luminaires as permitted in 410.117(C).
Exception No. 4: Lengths not exceeding 1.8 m (6 ft) from the last point where the raceway is securely fastened for connections within an accessible ceiling to luminaire(s) or other equipment.
 