bnbowen@uiuc.edu
Member
If I understand article 348.30 and it's exceptions correctly...... as an example, 1 inch greenfield can be as long as necessary,(if supported every 4.5 feet and 12 inches from each end) but if it is used for flexibility it can only be 3 feet long and supported 12 inches from each end. Is this correct? A contractor dropped EMT from the ceiling to a junction box and then ran 3 feet of greenfield to the connection box of a motor. The greenfield had a 12 inch clip connected to the JB (factory made). Should the greenfield be supported at the motor per 348.30,(A) and if so how? Thanks for your help, Brad