Support for MC Cable
gold7278
New member
I was recently told that MC cable should be supported no more than every four feet. I've always been told in the past, support for MC cable is between 5 and 6 feet.Can someone please confirm which is correct and post the corresponding article from the code which states proper distance. Thank you.
Re: Support for MC Cable
330.30 Securing and Supporting.
Type MC cable shall be supported and secured at intervals not exceeding 1.8 m (6 ft).
(A) Horizontal Runs Through Holes and Notches. In other than vertical runs, cables installed in accordance with 300.4 shall be considered supported and secured where such support does not exceed 1.8-m (6-ft) intervals.
(B) Unsupported Cables. Type MC cable shall be permitted to be unsupported where the cable:
(1) Is fished between access points, where concealed in finished buildings or structures and supporting is impracticable
(2) Is not more than 1.8 m (6 ft) from the last point of support for connections within an accessible ceiling to luminaire(s) [lighting fixture(s)] or equipment
(C) At Terminations. Cables containing four or fewer conductors, sized no larger than 10 AWG, shall be secured within 300 mm (12 in.) of every box, cabinet, fitting, or other cable termination.