mike harrison
Member
I'm confused. When I'm working with RMC, 344.30 (A), I am led to believe that all conduits entering a conduit body shall be supported on each conduit within 3' from the conduit body. 314.23 seems to imply the raceway can support the enclosure if utilizing RMC, as long as the openings to the conduit body are threaded, and the conduit body is of the same size as the trade size conduit. Please clarify the NEC in regards to conduit body support.