dedbrk said:
What I'm trying to express here is that the seismic support requirements for light fixtures comes out of the IBC and not the rules that our local L&I inspector governs (NEC, RCW or WAC). To my knowledge it is the building inspector that can make decisions on the proper seismic support of not only the suspended ceiling, but all systems installed in on or above such. The electrical inspector decides if the light fixture is supported properly. It can be supported independently of the grid system or it can be supported to the grid system by mechanical means such as bolts, listed clips, etc. if the framing members are securely fastened to each other and securely attached the building structure at appropriate intervals.
That's what I thought that you meant.
But you may not be too happy if you get what you're asking for. Let me explain.
We get this same type of situation with fire alarms. When an electrical inspector ignores items that are part of the building code but impact any electrical device installation, then what can happen is that after your electrical inspection
passes, the building inspector comes out and
fails the install, and you have to make corrections before a reinspection (reinspection fee #1).
But before the building inspector returns, he wants the reworked portions of the electrical to be reinspected by the electrical inspector (reinspection fee #2).
But if the electrical inspector catches it on his rough, corrections can be made, and then an electrical reinspection (reinspection fee #1) and the building inspector then comes out only one time.
You get less reinspection fees if the electrical inspector catches it up front.
The electrical item in the building code is required by the building inspector but inspected for proper installation by the electrical inspector since the NEC requires all electrical devices to be properly installed. The electical inspector must inspect
all electrical equipment that is installed for proper installation. It doesn't matter if they are devices required by the NEC, devices that are required by other codes, or devices that are not required but installed by customer choice.
David