support of emt

Status
Not open for further replies.

eelecduck

Member
Question from student,emt can be considered supported run horizontal above bar joist and secured with in 3 ft of a j box ,the question from student which he has done and was inspected and passed is it legal to use standard tie wire to secure conduit to bar joist within 3 feet of box? I said no it must be a listed type support fitting. I can not find a reference to tie wire ,has anyone have any thoughts on this subject. thank you eelecduck
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: support of emt

If you require the use of listed securing and supporting devices, then we have a big problem. Most of the devices commonly used for that purpose are not listed products. By the way, I think that the use of tie wire is often a much more secure method of securing and supporting raceways than the spring clips sold for the purpose.
Don

[ February 09, 2006, 07:17 AM: Message edited by: don_resqcapt19 ]
 

peter

Senior Member
Location
San Diego
Re: support of emt

Don't forget the glorious 5' exemption.
Perhaps the best [informal] test is what I call the handrail test. If you are up there walking on those slippery steel joists and start to lose your balance and you grab a run of EMT, will it save your neck or will some cheap, tin-can grade one hole strap spring open and expose you to the Newton's apple phenomenon?
Usually tie wire is 16 gauge and is black and oily and most electricians doub
le it up. It would be nice to have some galvanized, heavier gauge wire to work with. Scraps of #12 copper seem to work.
How about plumber's tape -- that 3/4" wide strip of steel with all the holes in it?
UniStrut is probably the strongest support we have. I agre that the Caddy clips are somewhat bogus but they do seem to satisfy the inspectors.
Wouldn't trust them to my handrail test though.
Instead of flat black, they should color code them. [This is experience talking: I just need one to affix 3/4" to a 1/8" bar joist and when I get up there, I discover that somebody tossed the wrong one into the wrong box.]
~Peter
 

GFH

Member
Re: support of emt

Best answer I ever got from an inspector about this was in the form of a question. He asked if it was tie-wire or bailing-wire? He caught me completly off guard so I asked him what differance that made. He relpied with a grin that bailing-wire was only allowed on farms and that as long as it was tie-wire I was okay to use it!
 

unimo

Member
Location
Colorado
isn't bailing wire a little heavier gauge and galvanized? might be good; of course we wouldn't call it that.
bailing wire and duct tape fix anything!
 

hardworkingstiff

Senior Member
Location
Wilmington, NC
Since it is above the bar joist, all you are doing is keeping the conduit from moving laterally, the weight is supported by the bar joist not the tie wire. Another option would be ty-wraps. Some of those have a 50-lb rating.
 