Support of Fire Alarm Cabling

Status
Not open for further replies.
Sorry for being so late on this post.
What's funny is Article 760 happens to be the only low voltage article that does require a spacing for supports. The only reference is made on 760.130,B,1 NEC 2008. This is also in the NEC 2005 but I can't tell you the Par. #. Book is in the truck. This requirement is 18" only for cables within 7' of the floor.
 