Support Wires

Status
Not open for further replies.

ruth

Member
Reference 1999 NFPA 70, Art 300-11(a). We don't allow conduit support wires connected to any part of the suspended ceiling grid. I understand (from several of our commerical electricans) that Washington State requires differing color ceiling wires (to diferentiate between ceiling grid/conduit supports, etc), fastened independently above, but tied to the ceiling support grid on the bottom. Seems to me if the ceiling falls down you've lost half of your support system. As we don't follow State rules, I may be a little in the dark here. Is that industry standard? Do other states allow tying the bottom wire of the conduit support system to the ceiling grid?
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: Support Wires

We work in a few areas that enforce that.

We avoid this by not using tie wires for support, we will use bridal rings.

Jumpers between lights we use the independent support wires that we are already required to put on the lights.

On jobs where we need to do this we use these clips and spray paint the wires while bundled.

12781294.jpg


Bob
 

websparky

Senior Member
Location
Cleveland, Ohio
Re: Support Wires

"Where independent support wires are used, they shall be secured at both ends."

Like Bob shows above.

We typically will wrap yellow tape around each wire to identify it.
 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
Re: Support Wires

If you don't tie them to the ceiling grid they are going to flop around. If you do then they support the ceiling. What's the difference between yours and the ceiling guys wires other than they are redundant? I suppose those Caddy clamps will limit the amount of pull and then let go but there is nothing in any code that says you have to use them.

I believe the reason for this is for if a firemen pulls the ceiling down the fixtures and everything else won't come down on him with it.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: Support Wires

The code only requires identification of conduit support wires when the ceiling is a "fire rated" assembly(300.11(A)(1). In normal ceilings, this identification is not required by the code(300.11(A)(2).

Ruth,
If you don't permit a connection to the ceiling grid, how are these supports "secured at both ends" as required by 300.11(A)?
Don
 