J jshaw2 Member Jan 12, 2004 #1 Can anyone point me in the right direction of using cable tray as means of support. I have a mechanical eng. that wants to support some water pipes from an existing cable tray. Weight wise the cable tray will support the added weight. Thanks
Can anyone point me in the right direction of using cable tray as means of support. I have a mechanical eng. that wants to support some water pipes from an existing cable tray. Weight wise the cable tray will support the added weight. Thanks
J jim dungar Moderator Staff member Location Wisconsin Occupation PE (Retired) - Power Systems Jan 12, 2004 #2 Re: Support Electrical cable trays are designed to support electrical cables only. They may not be used to support non-electrical systems.
Re: Support Electrical cable trays are designed to support electrical cables only. They may not be used to support non-electrical systems.
tom baker First Chief Moderator & NEC Expert Staff member Location Bremerton, Washington Occupation Master Electrician Jan 12, 2004 #3 Re: Support See section 692.3 Uses permitted. Note water pipes are not listed.
J jshaw2 Member Jan 12, 2004 #4 Re: Support Tom 692.3 is a section on Other Articles (Fuel Cell Systems). I am I missing something or did you mean another section?
Re: Support Tom 692.3 is a section on Other Articles (Fuel Cell Systems). I am I missing something or did you mean another section?
roger Moderator Staff member Location Fl Occupation Retired Electrician Jan 12, 2004 #5 Re: Support Jshaw, I think it's a typo. The article and section would be 392.3 Roger
tom baker First Chief Moderator & NEC Expert Staff member Location Bremerton, Washington Occupation Master Electrician Jan 12, 2004 #6 Re: Support Yes its a typo, thanks.