Supporting fire alarm cable to existing fire alarm conduit

Status
Not open for further replies.

JFletcher

Senior Member
Location
Williamsburg, VA
Technically speaking, there may be some small cases where you could strap fire alarm cable to conduit surrounding fire alarm cable. Practically speaking if somebody put the original Cable in RGS or IMT, then I think it stands to reason that any additional fire alarm cable should be inside the conduit and not strapped to it.

From a personal perspective, I learn the first week I was running cable to run independent support for it, do not strap it to existing plumbing, sprinkler pipe, electrical conduit, ceiling grid, anything. Support it independently.