C cvirgil467 Senior Member Location NewYork Sep 27, 2004 #1 Can junction boxes be supported from RGS conduit using at least two conduits without supporting the box from the building structure? Does section 370-23(e) of the 1999 NEC apply here?
Can junction boxes be supported from RGS conduit using at least two conduits without supporting the box from the building structure? Does section 370-23(e) of the 1999 NEC apply here?
iwire Moderator Staff member Location Massachusetts Sep 27, 2004 #2 Re: Supporting Junction Boxes Yes that applies and yes you can support the box if it has threaded entries.
Re: Supporting Junction Boxes Yes that applies and yes you can support the box if it has threaded entries.