Supporting with conduit.

Pinnie

Senior Member
Location
Ohio
Occupation
Commercial Electrician
Gentlemen, what is your opinion on using conduit as a mechanical means of support? Obviously, it’s generally not permitted when it’s used as a raceway. However, let’s say you want to hang a strip fixture, with aerial cable, from a piece of EMT that contains nothing and is installed specifically for that purpose. I could see an inspector having an issue with it, but I would argue that it’s not a conduit/raceway installed as part of the complete electrical system. Therefore, it’s just a mechanical means of support.
 
Nothing wrong with it all. It's no different than using another type of metal, wood or something else. In any case it's up to the AHJ to decide if it's adequate for the support.
 
Also, am I correct in my assumption that a conduit is just the name for the material, as if it were just laying on the ground and then a raceway is when it’s used as a complete part of an electrical system?
 
Although I've never done it, some can light rough in housings used to be built specifically to accept conduit supports.
Good way to use up the scrap laying around the job site.


Jap>
 
If I cut a short piece of EMT and use it as a sleeve it is not a raceway. If I cut a piece of EMT and use it to support a fixture it is not a raceway. If I pound a whole length of 3/4" RMC into the ground to use as a rod electrode it is not a raceway. The inspector should get it.
 
If I cut a short piece of EMT and use it as a sleeve it is not a raceway. If I cut a piece of EMT and use it to support a fixture it is not a raceway. If I pound a whole length of 3/4" RMC into the ground to use as a rod electrode it is not a raceway. The inspector should get it.

Although considered a "Sleeve" what defining factor does not allow a "Sleeve" to be considered a raceway?

Raceway - "An enclosed channel designed expressly for holding wires, cables, or busbars..."

Jap>
 
I don't know how that argument got started. In my circles, we called it all conduit or less formally pipe. EMT is just a variation of conduit, same as rigid, IMC or PVC.
I recall that debate but not the specifics. What is the reason for saying it is not conduit? The NEC does not define conduit. And does it effect anything if it were indeed not conduit?
 
I agree EMT is conduit to all of us that live in reality. In the world of wackiness and the NEC EMT is tubing. It's dumb. It did have some effect on some of the derating rules for a while until the code language was changed from conduit to circular raceways, or something like that. Someone who actually cares about this kind of stuff can explain it better.
 
I agree EMT is conduit to all of us that live in reality. In the world of wackiness and the NEC EMT is tubing. It's dumb. It did have some effect on some of the derating rules for a while until the code language was changed from conduit to circular raceways, or something like that. Someone who actually cares about this kind of stuff can explain it better.
Article 100 doesn't even define conduit or tubing. About the closest you'll get is the definition of conduit body which does mention the two distinct and different systems.
 
Just for fun here is the UL categories for conduit and tubing, note all conduit (342 thru 356) is under DWFV whereas tubing (358 thru 362) has it's own categories all starting with "F"


Electrical Metallic Tubing (FJMX)..................................................................................... 139 Electrical Metallic Tubing Fittings (FKAV) .................................................................... 139
Electrical Nonmetallic Tubing (FKHU) ............................................................................ 140
Electrical Nonmetallic Tubing Fittings (FKKY) ............................................................. 140

Conduit and Fittings (DWFV) ............................................................................................. 111Conduit and Cable Hardware (DWMU) ........................................................................ 111Conduit Fittings (DWTT) .................................................................................................. 111

Retrofit Fitting Kits Classified for Use with Extruded Rigid PVC Conduit(DWUC) ............................................................................................................................ 112

Flexible Conduit, Liquid-tight (DWWY) ........................................................................ 112
Flexible Metal Conduit Assemblies, Liquid-tight (DXAS) ...................................... 112
Flexible Metal Conduit, Liquid-tight (DXHR) .......................................................... 113
Flexible Nonmetallic Conduit, Liquid-tight (DXOQ) .............................................. 113
Flexible Metal Conduit (DXUZ) ....................................................................................... 113
Intermediate Ferrous Metal Conduit (DYBY) ................................................................ 114
Rigid Ferrous Metal Conduit (DYIX) .............................................................................. 114
Rigid Ferrous Metal Conduit with Polyvinyl Chloride Coating Verified for PVCAdhesion Performance (DYJC) ......................................................................................... 115
Rigid Nonferrous Metallic Conduit (DYWV) ................................................................ 115
Reinforced Thermosetting Resin Conduit (DZKT) ....................................................... 115
Rigid Nonmetallic Cellular Core Schedule 40 PVC Conduit (DZLR) ...................... 115
Rigid Nonmetallic Schedule 40 and Schedule 80 PVC Conduit (DZYR) ................. 116
Rigid Nonmetallic Underground Conduit, Plastic (EAZX) ........................................ 116
 
I agree EMT is conduit to all of us that live in reality. In the world of wackiness and the NEC EMT is tubing.
Dates back to when Jack Benfield invented EMT and tried to get the NEC to accept it. The NEC wouldn't accept it as conduit. It was tubing, thus the name Electrical Metallic Tubing. And I'm sure Jack didn't care what they called it as long as it sold.

-Hal
 
Dates back to when Jack Benfield invented EMT and tried to get the NEC to accept it. The NEC wouldn't accept it as conduit. It was tubing, thus the name Electrical Metallic Tubing. And I'm sure Jack didn't care what they called it as long as it sold.

-Hal
How sure are you that that is true? It just doesnt seem to make much logical sense. Without a definition of "conduit", it doesnt seem to make any sense to "not accept it as conduit" but accept it for use as long as it wasnt called "conduit".
 