As always, you need first to have proper electrical classification documentation. [Section 500.4] Once you have identified the proper classification(s), you are permitted to install any wiring method and equipment approved for that location. SO, what is the electrical area classification that the surface lights are actually in? Is that wiring method suitable for Class I, Division 2? [See Section 501.10(B)] There are a few cases where wiring and equipment above a classified location must be special, but that is generally not true for laboratories.