timm333
- Minneapolis, MN
- Electrical Design Engineer
What is difference between surge arrester for lightning surges, and surge arrester for switching surges?
Read all of the words...NEC article 280 is for surge arresters, and article 285 is for transient voltage surge suppressors. What would be the difference between the two?
280.1 Scope. This article covers general requirements, installation
requirements, and connection requirements for surge
arresters installed on premises wiring systems over 1 kV.
285.1 Scope. This article covers general requirements, installation
SPDs [surge arresters and transient voltage surge suppressors
(TVSSs)] permanently installed on premises wiring
systems 1 kV or less.
Was that a typo or are you confused?Jref, yes I see that article 280 is for >1kV, and article 285 is for <=1kV. So it is clear that article 280 will apply for switching surges. Switching surges originate internally within the structure, for example from switching of inductive loads.
280 will apply for switching surges inside your building only if your distribution voltage or load voltage inside the building is >1kV, and even then only if the devices are installed on the medium voltage portion of the system.....on premises wiring systems over 1 kV
No not confused, actually I believed that switching surges occurred only for nominal voltages above 1kV, so I said that for switching surges only article 280 will apply (not 285 because 285 is for nominal voltage below 1kV).
My other question is still unanswered, why do IEEE say (in attachment above) that switching surges should are prominent only for extra high nominal voltages of (>242 kV), while we know that large medium voltage motors can generate switching surges too.