I have plans that show surge arrestor fed from 3 phase 30A branch circuit breaker. The arrestor is three phase and grounded with grounding electrode conductor GEC of #6.
The cables provided from branch circuit panelboard breaker to the arrestor are 3 phase in one pvc conduit.
I asked the designer where is the equipment grounding conductor he says the surge arrestor is grounded no need for one.
I am not sure who is correct. I thought EGC are required for branch circuit. Am I correct or the designer? Any NEC 2014 code section that would backup if designer is correct?