I am searching for a surge protection system for a residential 200amp single phase transfer switch. The transfer switch doesn't have breaker spaces. There is no panel box between the meterbase and the transfer switch. So I am looking for a surge protector that could be installed "in line" on the service cables to protect the transfer switch. I have asked electrical suppliers. They only sell the type of surge protector that looks like a circuit breaker, and would be installed like a circuit breaker. Do they not make the "in line" type surge protector? Will I need to install a panel box between the meterbase and the transfer switch? I thought that a surge protector with service lugs might be available thereby eliminating the need to install a panel box between the meterbase and the transfer switch. I was wrong again?
 

Attachments

  • DSU 2B-00 - Installation of Whole-House Surge Protector.pdf
    85.1 KB · Views: 0
I am searching for a surge protection system for a residential 200amp single phase transfer switch. The transfer switch doesn't have breaker spaces. There is no panel box between the meterbase and the transfer switch. So I am looking for a surge protector that could be installed "in line" on the service cables to protect the transfer switch. I have asked electrical suppliers. They only sell the type of surge protector that looks like a circuit breaker, and would be installed like a circuit breaker. Do they not make the "in line" type surge protector? Will I need to install a panel box between the meterbase and the transfer switch? I thought that a surge protector with service lugs might be available thereby eliminating the need to install a panel box between the meterbase and the transfer switch. I was wrong again?
There is a class of SPD which is allowed to be connected directly to the service conductors upstream of the service disconnect. I do not have a reference for you though .
Other classes require connection downstream of the main OCOD or installation on a particular amp value protected branch circuit.

Sent from my XT1585 using Tapatalk
 
Status
Not open for further replies.
Top