I am doing a service upgrade and mounting a meter socket - then an offset nipple to a single 150A disconnect. With this install is it permissable to put the surge protective device in the indoor breaker panel?
1681760960885.png
 

Attachments

  • 1681760928635.png
    1681760928635.png
    22.9 KB · Views: 10
230.67(B) requires it to be at the service equipment which is the 150 amp disconnect. However the exception will permit it at the indoor panel.
 
So when did Article 230.67(B) appear? I don't think that it was in 2017 ?
If you are on a code older than the 2020, there is no code requirement to install a SPD. If you do, they are governed Article 285 and the manufacturer's instructions.
 