goldstar
Senior Member
- Location
- New Jersey
- Occupation
- Electrical Contractor
In a recent post I noticed the leads of a whole house surge protector landed on the service lugs ahead of the main along with the SEU wires. I believe, at one time in the minds of many electricians, this was a generally accepted practice. However, I don't believe this was ever allowed by the NEC. I'm sure the thinking was that if there was a power surge the installer wanted to make sure the surge protector worked without the possibility of interruption by a breaker.
That being said, most manufacturers today suggest that you land those wires on a 2-P breaker and as close to the main breaker as possible. It is my understanding that if a power surge occurs the over-voltage will spill off to ground via the MOV's within the unit. If I am wrong on this would someone please correct me ? Also, if there is an extreme power surge condition or a close lightening strike wouldn't the breaker trip leaving the panel unprotected thereafter ? I'm guessing if you get a direct lightening hit you can kiss it good bye.
That being said, most manufacturers today suggest that you land those wires on a 2-P breaker and as close to the main breaker as possible. It is my understanding that if a power surge occurs the over-voltage will spill off to ground via the MOV's within the unit. If I am wrong on this would someone please correct me ? Also, if there is an extreme power surge condition or a close lightening strike wouldn't the breaker trip leaving the panel unprotected thereafter ? I'm guessing if you get a direct lightening hit you can kiss it good bye.