Surge Protector - Type 3 - 30' Requirement

Status
Not open for further replies.
Can anyone tell me why there is requirement for type 3 surge protective devices (branch circuits) to be placed a minimum of 30' from the provided electrical service?

See article 285.25.

Thanks,
-greg
 
The impedance of the conductors between the service equipment and the surge protector is used to limit the surge current at the protector. There was another thread that had a post with more details but I don't have time to look for it now.
 