We were asked to a customers site to investigate several surge protectors that failed. The failer was charaterized by sever heat build up in the MOV board, melting of the plastic enclosure, smoke and damage to the desk top.
The devices were pluged into modular furniture. We suspected an open neutral and checked all internal furniture connections, branch circuit connections and visually checked the source panelboard.
We contacted APC (surge protector manuf.) and verified that this type of failer has been repoerted before and is cause primarily by an open neutral on a multiwire circuit creating an over voltage.
System is a seperatly derived via a 120/208v 3p4w 75KVA xfmr.
To date we have not found the root cause or evidence of an open nuetral.
There are two items we discovered that concern me.
1) The branch circuits have a seperate #12 equip. grounding conductor that terninates at the panelboard on a buss with non factory screw connections to the enclosure. There is no eq. gnding. conductor from the panel to the xfmer and we may have a high resistance ground. We are planning to test the resistance to ground via a clamp on ground resistance tester (AMEC 3711)
2) With the furniture completely disconnected (no load and phase, neutral and ground conductors disconnected) we have 6-8V betwenn N and G. This is true at the furniture connection and at the panel.
Any thoughts?
The devices were pluged into modular furniture. We suspected an open neutral and checked all internal furniture connections, branch circuit connections and visually checked the source panelboard.
We contacted APC (surge protector manuf.) and verified that this type of failer has been repoerted before and is cause primarily by an open neutral on a multiwire circuit creating an over voltage.
System is a seperatly derived via a 120/208v 3p4w 75KVA xfmr.
To date we have not found the root cause or evidence of an open nuetral.
There are two items we discovered that concern me.
1) The branch circuits have a seperate #12 equip. grounding conductor that terninates at the panelboard on a buss with non factory screw connections to the enclosure. There is no eq. gnding. conductor from the panel to the xfmer and we may have a high resistance ground. We are planning to test the resistance to ground via a clamp on ground resistance tester (AMEC 3711)
2) With the furniture completely disconnected (no load and phase, neutral and ground conductors disconnected) we have 6-8V betwenn N and G. This is true at the furniture connection and at the panel.
Any thoughts?