Surge suppression

Status
Not open for further replies.

goldstar

Senior Member
Location
New Jersey
Occupation
Electrical Contractor
I have a customer with a small photo lab in a strip mall. She recently purchased some computer based equipment and the company suggested she have surge suppression and lightening arrester equipment installed. My experience with this is to use the small canister type units that fit into a knock-out on the side of a breaker panel and terminated on a 2 pole breaker. If any one knows of a better type or system would you please point me in the right direction ? The panels are 150 amp, 3 phase 120/240 but she has no 3 phase equipment installed

Thanks in advance,

Phil
Gold Star Electric
 

dereckbc

Moderator
Staff member
Location
Plano, TX
Re: Surge suppression

The canister type you mention is a class A type TVSS. Class A is the smallest device and used to protect a branch circuit. You will need at least a class B or C device to protect a sub-panel or service panel.

My first question is this a sub-panel or a main service panel? If it is a service I would recommend a class C device. Sub-panel class B device.

When selecting a TVSS device look at the modes of protection, and surge rating in amps.

For class C device select a device that offers L-L, L-N, L-G, and N-G modes with at least 160K amps.

Class B, look for L-L, and L-N protection modes with at least 100K amps. Avoid L-G and N-G modes.

There are several manufactures out there (ACT, Dihn, LaMarche, Northern Technologies). Choose one that has hybrid modules meaning they have a combination of MOV, SAD, and or Gas. Gas absorbs the most energy, but take too long to operate. SAD is the fastest, but cannot handle large current. MOV's are fast and can handle large currents, just not as fast as SAD, or as much current as gas tubes. Best combo is MOV/SAD or SAD/GAS.

From an installation point of view twist the leads and keep them as short as possible. Lead length grater than 12 inches make the units worthless. Select a knock-out adjacent to first breaker nearest feeder or service. The best installation tip is buy a panel that has TVSS buit in using a Kelvin-Clamp method, or a device that is in front of the service or panel using Kelvin-Clamp. A Kelvin-Clamp is basically a bus with the protection modules bolted onto the bus with no leads.

[ April 07, 2003, 09:55 PM: Message edited by: dereckbc ]
 

goldstar

Senior Member
Location
New Jersey
Occupation
Electrical Contractor
Re: Surge suppression

Dereck,

Thanks for the info. This is a main lug, 3 phase panel. The main breaker is located at the far end of the building (approx 100' away)where the metering equipment is. So I guess we'll have to consider this a sub-panel. As far as terminating these devices there is no 3 phase equipment in the shop. Should I be terminating these devices on their own 100 amp, 3 phase breakers at the sub-panel ?

Thanks again,

Phil,
Gold Star Electric
 

dereckbc

Moderator
Staff member
Location
Plano, TX
Re: Surge suppression

If possible install a C device at the main, and Claas B at the sub. A TVSS device can only protect upto 80 feet of cable. If main is not possible install a class B or C at sub. Does not matter is there is no 3-phase equipment, protect all 3 phases.
 