I'll start off by saying that I work in a lab that has the sole purpose of identifying root causes of failed electrical components/systems. I am not an electrician by trade, so forgive my lack of knowledge of that side of things. I do have a EE degree so I'm not without some book-learnin' but my experience is not in field work.
A while back we had a facility that experienced the failure of several surge suppressors (power strips). These are the standard, 6ft cord, multiple plug outlets. (WABER/TRIPP-LITE) At the time of failure, three power strips were daisy chained together and a single laptop was plugged into the final strip. All three strips were burned identically. In each strip is a small circuit board with three MOVs and a couple thermal fuses. In all the strips, the same MOV (#2) was burned (melted and in some cases blown open). Not sure how to easily put up a schematic I have (PDF or Power Point) but it's the MOV between H and G.
Since the three power strips were all connected, it's not surprising they all had the same fault. And with no excessive load on them (1 laptop, still working), we figured it had to be a spike on that circuit somehow.
We checked all the other plugs on that circuit and found no damaged equipment.
On all the plugs we were measuring (AC)
H-G ~ 119
H-N ~ 116
N-G ~ 2.7
At one plug in the building we got almost 8V N-G.
Then we took measurements at the feeder panel... Very similar with the same ~2.5 VAC N-G But switching to DC it then reads 13.1V.
Obviously this didn't sound right to me, but it didn't explain my surge suppressor issue and the electrical crew was going to look into that N-G voltage. (I have yet to hear from them.)
Fast forward a few months and I get another call. Same building, same issue. Three more strips, each plugged in separate plugs, with no load plugged into them, all fried the same way.
No other facility has had issues. I'll try to track down the details on the supply transformers but wanted to see if I could get some thoughts.
A while back we had a facility that experienced the failure of several surge suppressors (power strips). These are the standard, 6ft cord, multiple plug outlets. (WABER/TRIPP-LITE) At the time of failure, three power strips were daisy chained together and a single laptop was plugged into the final strip. All three strips were burned identically. In each strip is a small circuit board with three MOVs and a couple thermal fuses. In all the strips, the same MOV (#2) was burned (melted and in some cases blown open). Not sure how to easily put up a schematic I have (PDF or Power Point) but it's the MOV between H and G.
Since the three power strips were all connected, it's not surprising they all had the same fault. And with no excessive load on them (1 laptop, still working), we figured it had to be a spike on that circuit somehow.
We checked all the other plugs on that circuit and found no damaged equipment.
On all the plugs we were measuring (AC)
H-G ~ 119
H-N ~ 116
N-G ~ 2.7
At one plug in the building we got almost 8V N-G.
Then we took measurements at the feeder panel... Very similar with the same ~2.5 VAC N-G But switching to DC it then reads 13.1V.
Obviously this didn't sound right to me, but it didn't explain my surge suppressor issue and the electrical crew was going to look into that N-G voltage. (I have yet to hear from them.)
Fast forward a few months and I get another call. Same building, same issue. Three more strips, each plugged in separate plugs, with no load plugged into them, all fried the same way.
No other facility has had issues. I'll try to track down the details on the supply transformers but wanted to see if I could get some thoughts.