Surging Phone Lines for Fire Alarm Panels
For the POTS lines for Fire Alarm Systems, what NEC code section specifically says the phone lines must be surged prior to entering the fire panel dialer? Or, is this not a code requirement? I am not talking about any type of protection the public utilities puts on their lines at the point of entry into a building. I'm talking about the phone lines from the utilities point of demarcation to the fire panel itself. Is a surge required on the phone lines at fire panels? The NFPA-72 National Fire Alarm Code refers you right to the NEC as follows.
The National Fire Alarm Code, Reference: NFPA 72, 2002 Edition, Chapter 4, Paragraph 4.4.4.3) states:
4.4.4.3 Transient Protection. To reduce the possibility of damage by induced transients, circuits and equipment shall be properly protected in accordance with the requirements of NFPA 70, National Electrical Code, Article 800.
Thank You.
For the POTS lines for Fire Alarm Systems, what NEC code section specifically says the phone lines must be surged prior to entering the fire panel dialer? Or, is this not a code requirement? I am not talking about any type of protection the public utilities puts on their lines at the point of entry into a building. I'm talking about the phone lines from the utilities point of demarcation to the fire panel itself. Is a surge required on the phone lines at fire panels? The NFPA-72 National Fire Alarm Code refers you right to the NEC as follows.
The National Fire Alarm Code, Reference: NFPA 72, 2002 Edition, Chapter 4, Paragraph 4.4.4.3) states:
4.4.4.3 Transient Protection. To reduce the possibility of damage by induced transients, circuits and equipment shall be properly protected in accordance with the requirements of NFPA 70, National Electrical Code, Article 800.
Thank You.