Good afternoon Everybody,
If you have a 277/480V, 3P, 4W, 200Amp MCB SUSE rated panel mounted on a unistrut would you need to bond to building steel and cold water pipe to complete grounding system if the building steel and cold water pipe are 100' away minimum? Wouldn't this be considered not "available"...
I was going to provide a #4 ufer or (2) 3/4" x 10'-0" ground rods minimum of 6' apart (& not bond the neutral and ground bus as this has been done upstream at it's source).
appreciate your input