I know it is in the new code somewhere concerning securing wire in drop ceilings. Could you guide me to it. And does low voltage(12v) need to be secured??
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: suspended ceilings

Look at 300.23, 725.5, 760.5, 770.7, 800.5 or 820.5. One of those sections should cover your application.
Don
 