Suspended unistrut support

Status
Not open for further replies.

Fcollins

New member
Location
Texas
I couldn't find this in the code book, but if you are hanging 20 foot pieces of unistrut in a continuous 60 foot run suspended from 3/8 all thread, what is the maximum spacing allowed between all thread hangers. The unistrut is support track lighting.
 
I couldn't find this in the code book, but if you are hanging 20 foot pieces of unistrut in a continuous 60 foot run suspended from 3/8 all thread, what is the maximum spacing allowed between all thread hangers. The unistrut is support track lighting.

Check the design section of the Unistrut manual. You will need to calculate the load on the Unistrut to determine the number and spacing of the anchors you use, which will also depend on whether you are attaching to a concrete deck, corrugated metal deck, bar joists, "Z" or "C" purlin, etc.
 
Unistrut Engineering

Unistrut Engineering

This will not be in a code book, as there are numerous circumstances that must be accounted for. One major one is the load, with the attachment being just as important.

Please do not hesitate to contact Engineering at Unistrut Ohio and I will personally help you out. {Anyone requiring personal contact with Matt can do so using the PM feature}
 