On new above grnd. pools, most of the metal parts are covered in pvc or plastic. How do you or do you bond all covered parts or is one attatchment to a dedicated lug all that is neccessary w/#8 solid to the motor lug? (also bonding metal deck, ladder, etc.). Also, is the circuit "groundING" conductor not to be attatched to this #8 solid? (#12 wire)
Also, is the circuit "groundING" conductor not to be attatched to this #8 solid? (#12 wire)
That question made my head hurt.
It's so hard to answer a question when "shorthand" is used. . You can't look up "groundING conductor" in the NEC. . You can't find out the requirements for a "#8". . And you can't find out the requirements for a "#12".
You've got to get these categories straight and drop the "shorthand" or you'll never get to the right spots in the NEC.
The jobs of bonding [and grounding] wires are separated into 3 main categories
1] electrode
2] equipotential
3] equipment
1] electrode, 250.32 says, "Building(s) or structure(s) supplied by feeder(s) or branch circuit(s) shall have a grounding electrode ..... installed .....". . Is the pool a "structure" ? . Yes. . Is it supplied by more than "a single branch circuit" or a shared neutral "multiwire branch circuit" ? . Usually. . Should this rule apply to a pedestal mounted pool feeder panel ? . My answer is yes. . But don't confuse a electrode requirement with a equipotential requirement.
A ground rod is an
electrode. . It's conductor goes to the
panel enclosure. [250.32(B) connected to the ..... disconnecting means]
2] equipotential, When you say "#8" you're probably talking about
equipotential, which bonds to the
motor housing. . This would also bond to the lug on the
outside of any wet niche fixture and also to all pool metal and also to the pool
deck/sidewalk structure. [680.26(B)(1)-(7)]
3] equipment, Your
equipment ground [grounding conductor] is required to be #12 or larger insulated copper run
with the other circuit/feeder conductors. [250.134(B), 300.3(B)]. . The equipment ground for a light niche nonmetalic conduit is required to be #8 and insulated [680.23(B)(2)(b)]. . The equipment ground for the light has limits on joints and splices [680.23(F)(2)]. . The bond lug on the
inside of the wet niche fixture is for equipment ground and must be "encapsulated in, a suitable potting compound". [680.23(B)(4)]
Notice that pool
electrode questions are answered mainly in 250.50,
pool
equipotential questions are answered mainly in 680.26,
and pool
equipment ground questions are answered mainly in 680
before .26
Getting back to your question:
Also, is the circuit "groundING" conductor not to be attatched to this #8 solid? (#12 wire)
If I
assume that you mean:
Also, is the circuit
equipment grounding conductor (#12 wire) not to be attached to this #8 solid
equipotential bonding conductor ?
If my assumption is right, the
only time that the pool equipment and equipotential grounding conductors terminate on the same point is 680.26(B)(6)(a), Double-Insulated Water Pump Motors. . Otherwise the equipment ground terminations are inside the equipment with the other circuit conductors. . Equipotential lugs are found on the outside of the equipment.