Of the main is staying would you remove and reinstall these (2) 800A and (1) 400A breaker while gear is live or is that way too dangerous? It's 120/208v so thinking that does make a difference as 277/480 would def be a no no Thanks



1759502636814.png
 
If that is an FPE panel those branch breakers are bolted in. Dealing with nuts and washers goes a lot faster when you aren't worried about dropping them into live bussing.
 
If it was a SqD I-Line maybe, but no way on a bolt in FPE. Plus the Arc hazard and PPE would be a pain compared to simply notifying the tenants and doing it during "non-work" hours.
 
I-Line breakers are basically "plug-in" as opposed to FPE bolt-in (bolted to buss) so I-Line would be safer top exchange but OSHA rules apply to both.
 