I have a project where we installed a digital revenue meter (SEL-735) on a service entrance breaker, connected to a set of PTs (wye connected) and CTs (also wye connected). The power flow is from the utility to the load (no generation). The meter is currently reading positive kW. However, the customer is asking for the meter to read negative kW. There is no option to program this change in this specific meter, so a wiring change will be needed.
I requested our contractor to swap the wiring directly on the meter to reverse the polarity of the CTs. However, I've received some pushback, stating that the power factor will be off due to this swap, and essentially putting the current 180 degrees apart from the voltage.
I believe the swap will put both KVAR and KW into a negative quadrant, and thus creating an accurate PF, but I'd like some additional opinion if there is something that I'm missing in this analysis?
I requested our contractor to swap the wiring directly on the meter to reverse the polarity of the CTs. However, I've received some pushback, stating that the power factor will be off due to this swap, and essentially putting the current 180 degrees apart from the voltage.
I believe the swap will put both KVAR and KW into a negative quadrant, and thus creating an accurate PF, but I'd like some additional opinion if there is something that I'm missing in this analysis?