SWBD remaining active w/less sets

Status
Not open for further replies.

mstrlucky74

Senior Member
Location
NJ
If I have a main switch in a main switchboard feeding another switchboard with say with 3 sets of 750's and you denergize/disconnect one of the sets there is no way the switchboard could remain live with just two sets feeding it if the 3 sets were sized correctly? Thanks

Sent from my SM-G955U using Tapatalk
 

mstrlucky74

Senior Member
Location
NJ
If I have a main switch in a main switchboard feeding another switchboard with say with 3 sets of 750's and you denergize/disconnect one of the sets there is no way the switchboard could remain live with just two sets feeding it if the 3 sets were sized correctly? Thanks

Sent from my SM-G955U using Tapatalk
Sorry guys...can mod move this to engineering forum.ty

Sent from my SM-G955U using Tapatalk
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
You would need to change the OCPD ahead of the two sets to a size that was code complaint for their reduced ampacity. Also you would need to ensure that the existing load does not exceed the smaller OCPD size.
 