SWBD Sections

Merry Christmas

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The fire pump section has to be isolated from the rest of the sections.
True if the fire pump switch is part of the switchboard. His drawing shows a tap section for both the fire pump and the fire alarm. I would assume that these "tap" conductors go to separate disconnect switches.
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
True if the fire pump switch is part of the switchboard. His drawing shows a tap section for both the fire pump and the fire alarm. I would assume that these "tap" conductors go to separate disconnect switches.
I'll buy that.
 