SWD and HID Circuit breakers

Status
Not open for further replies.
In article 240.83(D) it talks about swd or hid rated breakers for control of lighting circuits being panel switched are all breakers rated for this or is this someting thant need to be called out specifically when you do panel schedules and have breakers being used as switches?? :confused: :confused:
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: SWD and HID Circuit breakers

These breakers are only used for switching HID or FL lighting. SWD breakers are no longer available from mfgs, they are replaced by HID, which can be used on both locations. If you are not switching the lighting with the breakers then a standard breaker can be used.
 