djankly
New member
- Location
- los angeles CA
Hi and thanks for having this forum! Let me start off by saying I am a homeowner (LA County) with 3 young kids, and I don't touch the electric...
We recently completed construction on an in-ground pool with concrete shell and deck. All the pool equipment (including the electric sub-panel for the pool) is a minimum 10ft from the pool water. All electric has been properly grounded. The pool passed the equipotential bonding inspection prior to pouring the deck.
Only thing holding up final inspection is that the inspector says the bonding grid must be physically connected to the pool equipment. What is the rule here? If the equipment is 10 feet away does the bonding wire need to be connected to the equipment?
If so, can't the ground lines be considered as a bond lines as well? Seems to me that since everything (lights-which are connected to the equipotential grid and the ground at the subpanel, pool equipment and all other electric) is connected (grounded together) at the panel they all have the same equipotential. Shouldn't this satisfy the bond requirement?
This pool project has been an absolute 6-month nightmare because of the contractor and any help would be greatly appreciated! It will take at least a month for he contractor to get back to me...Dan
We recently completed construction on an in-ground pool with concrete shell and deck. All the pool equipment (including the electric sub-panel for the pool) is a minimum 10ft from the pool water. All electric has been properly grounded. The pool passed the equipotential bonding inspection prior to pouring the deck.
Only thing holding up final inspection is that the inspector says the bonding grid must be physically connected to the pool equipment. What is the rule here? If the equipment is 10 feet away does the bonding wire need to be connected to the equipment?
If so, can't the ground lines be considered as a bond lines as well? Seems to me that since everything (lights-which are connected to the equipotential grid and the ground at the subpanel, pool equipment and all other electric) is connected (grounded together) at the panel they all have the same equipotential. Shouldn't this satisfy the bond requirement?
This pool project has been an absolute 6-month nightmare because of the contractor and any help would be greatly appreciated! It will take at least a month for he contractor to get back to me...Dan