For a swimming pool, there is supposed to be an intentional bond in contact with the pool water.
680.26(C) (2011):
Normally metal ladders and other metal items in the pool would satisfy this requirment.
If I don't have any of these metal items in the pool, does concrete meet the requirement of being a "conductive surface"?? (The concrete will have either bonded rebar or a copper conductor grid installed in it.)
If not, the handbook says that there are devices that are specifically listed for this purpose. Does anyone know who makes them or what they are called?
680.26(C) (2011):
Code:
An intentional bond of a minimum conductive surface area of 9 square inches shall be installed in contact with teh pool water. This bond shall be permitted to consist of parts that are required to be bonded in 680.26(B).