I am experiencing difficulties with a swimming pool heat pump tripping breakers. The name plate on the heat pump says 208/230 volts, 60 Hz, 29 R.L.A., 38 amp minimum circuit ampacity. With an amp meter connected, the compressor kicks on and after starting, registers 30 amps and then begins slowly climbing and ends up at 49 amps after 45 minutes. The manufacturer's tech rep says this is typical. Even though the manufacturer's own material recommends a 40 amp breaker for this device, it is insufficient. It is wired with #8 and will operate fine with a 50 amp breaker. My question is, aren't there any rules or laws governing innacurate name plate data? And, isn't the R.L.A. supposed to be the normal operating amperage of this device? The tech rep says I could put a 70 amp breaker on it if I wanted to. Does the manufacturer not have to be more specific in sizing the overcurrent device or is the 30 amp range they are giving me normal?