Swimming pool load center
bluecollar84
US
How close can I mount a swimming pool 3r load center to my pool wall? Distance in feet and code article ? Also can I run pvc conduit underground to feed it from the house ?
This would apply since the pool disconnect is in this panel.
680.12 Maintenance Disconnecting Means. One or more
means to simultaneously disconnect all ungrounded conductors
shall be provided for all utilization equipment other
than lighting. Each means shall be readily accessible and
within sight from its equipment and shall be located at least
1.5 m (5 ft) horizontally from the inside walls of a pool,
spa, fountain, or hot tub unless separated from the open
water by a permanently installed barrier that provides a
1.5 m (5 ft) reach path or greater. This horizontal distance is
to be measured from the water’s edge along the shortest
path required to reach the disconnect.
Yes