jeff1166

Member
Is it required to GFCI protect a 120-volt or 220-volt pool motor that is hard wired? I know a plug in connection for the motor needs a GFCI.
 
Re: Swimming pool motors

jeff

I say yes that it does not matter whether is is cord-plug or hardwired, see art 680-5 it would need a GFCI
 
Re: Swimming pool motors

680.5 Ground-Fault Circuit Interrupters.
Ground-fault circuit interrupters (GFCIs) shall be self-contained units, circuit-breaker or receptacle types, or other listed types.
680.22(5) Area Lighting, Receptacles, and Equipment. GFCI Protection. All 125-volt receptacles located within 6.0 m (20 ft) of the inside walls of a pool or fountain shall be protected by a ground-fault circuit interrupter. Receptacles that supply pool pump motors and that are rated 15 or 20 amperes, 120 volt through 240 volts, single phase, shall be provided with GFCI protection.
For now I may be overlooking the part where a hard-wired swimming pool pump must be GFCI protected.
 
Re: Swimming pool motors

In the 99 NEC 680-6(d) Required motors that were hard wired, in other than dwellings to be GFCI protected.
I can't even find that in the 2002 NEC, so I'd say no, if you are useing the 2002.
 
Re: Swimming pool motors

Folks
I should have edited my post to clearify the code year we are using I am in Virginia and we are still using the 1999 code at this time.
Sorry AWWT for the confusion,
 
Re: Swimming pool motors

Alrighty then is this a dwelling or other than a dwelling?
 
rickcham said:
I should have edited my post to clearify the code year we are using I am in Virginia and we are still using the 1999 code at this time.
Um, Rick, I have some news for you: We adopted the 2002 NEC last November, as in November of 2005.

Unless you pulled that permit over a year ago . . . well, let's just say it's time to trade that white book in on a red one.
 