680.5 Ground-Fault Circuit Interrupters.
Ground-fault circuit interrupters (GFCIs) shall be self-contained units, circuit-breaker or receptacle types, or other listed types.
For now I may be overlooking the part where a hard-wired swimming pool pump must be GFCI protected.680.22(5) Area Lighting, Receptacles, and Equipment. GFCI Protection. All 125-volt receptacles located within 6.0 m (20 ft) of the inside walls of a pool or fountain shall be protected by a ground-fault circuit interrupter. Receptacles that supply pool pump motors and that are rated 15 or 20 amperes, 120 volt through 240 volts, single phase, shall be provided with GFCI protection.
Um, Rick, I have some news for you: We adopted the 2002 NEC last November, as in November of 2005.rickcham said:I should have edited my post to clearify the code year we are using I am in Virginia and we are still using the 1999 code at this time.
Incredible first post!Dinspect said:Water and electricity do not mix!